Hello all,
I am new to posting here, but after rummaging around this thread for years, I though I'd clarify something that's been bothering me. I know and understand ( I think) article 314.16 but don't understand why something like a "switch" box (ie 3x2x2.5/ 12.5 in3) can't even live up to the marketed name. Seems to me like you can't use it for anything other than an end receptacle or a basic SP switch (leg only, not fed trough). Am I wrong?
For example, 12awg BX in 3x2x2.5 "device" box assuming internal clamps used as a switch box for a feed through configuration would yield 2+2+1+1+2= 8*2.25=18in3, not allowed.
Or even a 4x2 1/8x1 7/8 handy box as a an end point for a three-way would only be OK if the neutral never sees the inside of the switch box (B+R+G+switch = 5 the maximum allowed!).
Why are these boxes so widely marketed (and used) when they seem to be almost useless. I know they can be used as pulls and JBs on smaller circuits, ect.
Thanks!
dp
I am new to posting here, but after rummaging around this thread for years, I though I'd clarify something that's been bothering me. I know and understand ( I think) article 314.16 but don't understand why something like a "switch" box (ie 3x2x2.5/ 12.5 in3) can't even live up to the marketed name. Seems to me like you can't use it for anything other than an end receptacle or a basic SP switch (leg only, not fed trough). Am I wrong?
For example, 12awg BX in 3x2x2.5 "device" box assuming internal clamps used as a switch box for a feed through configuration would yield 2+2+1+1+2= 8*2.25=18in3, not allowed.
Or even a 4x2 1/8x1 7/8 handy box as a an end point for a three-way would only be OK if the neutral never sees the inside of the switch box (B+R+G+switch = 5 the maximum allowed!).
Why are these boxes so widely marketed (and used) when they seem to be almost useless. I know they can be used as pulls and JBs on smaller circuits, ect.
Thanks!
dp