Dusty Steele
Member
- Location
- Austin Texas
- Occupation
- Electrician/Electrical Inspector
This is more of a general question about box fill. I have a 4" X 4" X 4" junction box with a hinged cover. There aren't any visible markings as to what the cubic inch allowance is for this box. The conductors entering into the box are: 6) #8awg & 5) #10awg. Which calculates to 30.5 cubic inches. There are only 3) #10awg EGC'S which has been captured in the "5) #10awg". The largest 4 square (2 1/8" deep) listed in Table 314.16(A) is only 30.3 cubic inches. Does anyone have any code references or standards that will help me out with the question of how do I calculate and what is the allowable box fill?