Does not matter, all clamps in total equal 1 conductor allowance.
Yup, per 314.16(B)2. FWIW here is an old FAQ from carlon: http://www.carlon.com/FAQs/FAQ-ZipBoxes.pdf
Does not matter, all clamps in total equal 1 conductor allowance.
How many of these clamps would be required to take up 2-2.25 cubic inches?
If you guys are putting so many wires in one of those boxes that you have to worry about how much the clamp takes up.....Stop doing that.
I called Pass and Seymour about this issue just for fun and they got back to me today. They said the clamp must be counted. The only reason they put the conductor numbers in are for marketing purposes. So do the calcs just as you would any other box with clamps.
So would anybody count a RX connector in a 4" sq. box? Code seems to say it is not necessary and you know that clamp takes up more space then the ones in the P&S boxes. What is confusing is the clamps are there and I assume the cu. in is measured with the clamps there so why must be deduct.
I actually did a crude measure on the 22.5 cu. in box and I got 22.34 without deducting the clamp. Accuracy is not great but it is close.
I will continue to not count them in my calculations. I make it a point not to max out my boxes, but until they differentiate the volume allowance between a 15A single pole switch and a GFCI receptacle or dimmer, the volume difference with these clamps is hardly worth worrying about.
If you guys are putting so many wires in one of those boxes that you have to worry about how much the clamp takes up.....Stop doing that.
That is correct it used to be one wire for a device and now it is 2 specifically because of dimmers, GFCI receptacles and the like.Make a proposal. The CMP is not totally adverse to the idea. Read the panel statement in this one.
So, do you count the clamps in plastic boxes? Do you enforce it as an inspector?