Where is the 6X rule in the NEC? If I remember correctly there are requirements for bending space at terminals but not for the individual conductors.
334.24 Bending Radius. Bends in Types NM, NMC, and NMS
cable shall be so made that the cable will not be damaged. The
radius of the curve of the inner edge of any bend during or
after installation shall not be less than five times the diameter
of the cable.
I am sure there is one for conductors-- I will look