No kid jokes.
http://ecmweb.com/nec/2017-national-electrical-code-changes?page=10
See underlined revision
(3) Smaller Dimensions.
Listed boxes or listed conduit bodies of dimensions less than those required in 314.28(A)(1) and (A)(2) shall be permitted for installations of
combinations of conductors that are less than the maximum conduit or tubing fill (of conduits or tubing being used) permitted by Table 1 of
Chapter 9.
Listed conduit bodies of dimensions less than those required in 314.28(A)(2), and having a radius of the curve to the centerline not less than that
indicated in Table 2 of Chapter 9 for one-shot and full-shoe benders, shall be permitted for installations of combinations of conductors permitted
by Table 1 of Chapter 9. These conduit bodies shall be marked to show they have been specifically evaluated in accordance with this provision.
Where the permitted combinations of conductors for which the box or conduit body has been listed are less than the maximum conduit or tubing
fill permitted by Table 1 of Chapter 9, the box or conduit body shall be permanently marked with the maximum number and maximum size of
conductors permitted.
For other conductor sizes and combinations, the total cross-sectional area of the fill shall not exceed the cross-section
area of the conductors specified in the marking, based on the type of conductor identified as part of the product listing.
Informational Note: Unless otherwise specified, the applicable product standards evaluate the fill markings covered here based on
conductors with Type XHHW insulation.