Well I figured I’d give you an update now that the project is complete and passed inspection. Ended up going with 600 MCM with a 500mcm neutral at the mast. The neutral is larger than needed but it was what I access to at the time . I had a good discussion with PSE about paralleling 4/0. It was recommended that I do not go this route. They said “
Yes you can go this route but they’ve had issues with the taps at the weather head causing issues with parallel lines”. Long story short, I only wanted to deal with this one time so that was out. The ATS that I got ended up having a 200 amp disconnect so that saved me some equipment and time. Went with a number 6 ground to two rods protected by half inch conduit. Used 4/0-2/0 to feed the two 200 amp disconnects. FYI The inspector did say that he believes I could’ve went with 500 MCM with a 350mcm neutral. I did not drive too far into this conversation with him so I’m not sure how that would have turned out. I think looking at the NEC that would have not met the requirements But I’m not putting any more research into it.
On a different note I had a discussion with the inspector on exterior disconnects. We looked up the code together and Washington’s WAC. The disconnects at the pole will count as my exterior disconnects as long as the panels inside the house can be accessed within 15 feet of the entrance. I believe this is allowed because of the Washington code. The inspector and me talked about it for 15 minutes then he called two other inspectors and this is what we came up with. It was an interesting conversation so I thought I’d pass it on.
All that’s left is to run the wire from the pole to the house. Going with 4/0-2/0 with a 4awg AL ground For the two runs to service the house. I search the NEC and did not find anything about separation requirements on the two feeds to the house. Anyone have any input here? I plan on putting them in the same 36” deep ditch and separating them by about 12 inches, surrounded in sand.
View attachment 2560140