Re: 320 watts
You are driving this conversation to a level of math that I don?t think you want to get anywhere near. But you are also using invalid simplifications. So I?ll try to clarify a few things. I might not succeed in making it more clear, but I?ll try.
What I said is that you can take any signal, be it a power or a voltage or a financial or a set of sports scores, and calculate the RMS value of that set of numbers. I also said that if the original values followed a standard sine wave, then the RMS value is going to be 70.71 % of the peak value.
That 70.71% rule does not apply, if the original signal is not a sine wave. In a single phase AC circuit, even one with a purely resistive load, ?power? is not a sine wave. Therefore, you can?t use the 0.7071 factor. To get the RMS value of power, you have to start with the numbers that represent the moment-by-moment values of power. You get those by taking the moment-by-moment values of voltage and of current, and multiplying them. This is the set of numbers with which you do the ?square, then average, then square root? process.
If there are inductive or capacitive loads (i.e., if the power factor is not 1.0), then the voltage and current do not reach their peaks at the same time. In that case, multiplying (Vpeak) by (Ipeak) will not give you anything closely related to (Ppeak)

You are driving this conversation to a level of math that I don?t think you want to get anywhere near. But you are also using invalid simplifications. So I?ll try to clarify a few things. I might not succeed in making it more clear, but I?ll try.
What I said is that you can take any signal, be it a power or a voltage or a financial or a set of sports scores, and calculate the RMS value of that set of numbers. I also said that if the original values followed a standard sine wave, then the RMS value is going to be 70.71 % of the peak value.
That 70.71% rule does not apply, if the original signal is not a sine wave. In a single phase AC circuit, even one with a purely resistive load, ?power? is not a sine wave. Therefore, you can?t use the 0.7071 factor. To get the RMS value of power, you have to start with the numbers that represent the moment-by-moment values of power. You get those by taking the moment-by-moment values of voltage and of current, and multiplying them. This is the set of numbers with which you do the ?square, then average, then square root? process.
That part is right, but only because you are talking about resistive loads.Originally posted by coulter: Well, one approach is: The power delivered to the load is .707Vpeak X .707Ipeak = (1/2)(Vpeak)(Ipeak)
That part is also right, but again only because you are talking about resistive loads.(1/2)(Vpeak)(Ipeak) = (1/2)(Peak Power)
If there are inductive or capacitive loads (i.e., if the power factor is not 1.0), then the voltage and current do not reach their peaks at the same time. In that case, multiplying (Vpeak) by (Ipeak) will not give you anything closely related to (Ppeak)
You are right. It?s not. Nor is there any reason to expect that it would be. My integral calculus is a bit rusty, but I calculated that the RMS value of power delivered to a single phase resistive the load was about 61.24% of the peak value of power. I had to find a table that gave me an expression for the ?indefinite integral of cosine raised to the power of 4.? Wanta see it?Originally posted by coulter: The power delivered to the load is . . . (not) .707 (Ppeak)