Re: 3200 amp service
Kevin
I read 250.24(B)(1) A little differently
, the grounded conductor shall not be smaller than 12? percent of the area of the largest service-entrance phase conductor.
The grounded service entrance conductor of a 3-phase, 3-wire delta service shall have an ampacity not less than the ungrounded conductors.