- New Jersey
- Journeyman Electrician (retired)
Anyone have an idea what you would use a transformer with this output for?
A new one for me.
Same here. And thanks, now I can say I have indeed seen it all![]()
A new one for me.
PS: I find it very odd that some countries are listed as using 380Y/220 while others use 380Y/200. It does not seem possible for both of those to be right!
325Y/188 at least has the right ratio.![]()
Wrong direction. 380/50 = a V/Hz ratio of 7.8:1, 480/60 = 7.67:1. You don't need a transformer to make a 380/50 motor to work correctly (albeit faster) when applied to 480/60....
B. A 380V 50Hz motor would need 380 x (5/6) to maintain the V/F ratio to operate at full load without a VFD. That is 316. ...
....so this was likely a spare transformer for an OEM machine put on a shelf just in case, but when the system failed, it was replaced with something newer that no longer needed that transformer.