controlsguy
- DFW
I am looking for a second opinion on how 330.12 (1) applies to type MC-HL or Okonite C-L-X when installed in an installation open to authorized personnel only. The application's goal is to replace a cable tray or conduit and wire system with MC-HL (CLX) supported by process piping and process piping supports in lieu of an independent support system. This is a power limited (controls) installation with the cable being installed in the following manner:
1. direct burial
2. affixed to process piping and process piping supports in lieu of an independent support system.
3. passing through and also terminating in class 1, div 1 and div 2 locations.
I believe that MC-HL or CLX is an acceptable wiring method for this application when terminated and supported appropriately except where the cable might be exposed to physical damage at the lower (near ground level) elevations of the proposed installation. The "physical damage" risk at the lower elevations would be from personnel working on the equipment and not truck or equipment traffic.
Would the crush rating of the MC cable or installation of gaurding around the lower elevations in lieu of cable tray or conduit negate 330.12 (1)?
Thanks in advance for your help.
1. direct burial