Thanks for finding and posting the ROP. Looks like their service loop is allowable, although I will still "red-tag" it if it isn't kept tidy.
I hope the commercial wiremen don't start this practice because EMT is worded similarly ambiguous.
I rue the day when I have to pass an installation where someone leaves a box, travels 2', turns a double 90 and goes out past the original box with the first support only 3' away, but in actuality has 8' of EMT in the run.
:jawdrop:
:happysad:
I agree, I see it as asinine too.
BUT, the CMP clearly stated it's allowed.
Please go back and look at the ROP I posted, the panel statement is aimed at all of 334.30, not just one of the subsections.
:jawdrop:
:happysad:
Conduit doesnt need a service loop; any impossibly short conductors can be repulled from A to B.
I'm most curious under what section you'd red-tag a messy or untidy service loop. If you're going to cite "neat and workmanlike", this thread is nothing compared to that can of worms. :D
Seriously, or more seriously, that there can even be a debate on this is proof enough to me that this section (334.30) needs to be re-written.
If the loop of NM puts the cable at risk of physical damage, then I would have justification.
Nothing in the code allows a service loop for fixed in place fixtures, only drop in ones. Same ambiguous language allows conduits to be run longer than 3' before the first support.