In reading 334.80 I have a question. Does this section prohibit running more than 2, 12-2 nm's in a bored hole if there is insulation in the wall? And if there is no insulation in the wall you can run as many as you want?
Thanks. What about when it refers to thermal insulation? Is this refering to insulation in the wall cavaties?
We can in fact have 3- 12/2 and one 12/3 without an issue for the same reason.
Dennis,
I have only applied this rule when the hole itself is "caulked" (sealed), not when there is only wall thermal.
(a mute point here as the building inspectors require that hole to be caulked)
Do you see it differently ?
Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).
This is true also. I didn't feel the need to cover every scenario as there are other possibilities also.In many cases you could run 4-12/3 cables through that same hole and still only have 8 CCC's.
You must also consider what is the load on the conductors, just like you would if you were running the conductors in a raceway.
If you have known fixed load less than 15 amps on several 12 AWG cables you could run more than 4 12-2 cables. You could in fact run 10 cables through the same hole. This could be the case with say several baseboard heater circuits.
Can you quote an article that supports what you say. I hear you but that is not what the code states.
I believe you are right. Thanks.I think that he meant this:
#12 conductors = 30amp @ 90?
10-2 wire cables = 20 CCC's
10-20 CCC's = 50% derating
30 amps * 50% = 15 amps
OK for 15 amp OCPD.
Should be ok for 20 amp OCPD if supplying a fixed load that is less than 15 amps. The fixed load will not change no matter what the OCPD is. Which is what I was getting at in my post. 310.15 is about conductor ampacity not overcurrent protection. Many inspectors would see ten cables in the hole(s) and immediately say you can't do that. But there are conditions where you could. They need to question what is going on before jumping to conclusion that it can't be done.
This is what I thought you were saying but I thought I read it wrong. You cannot have 10 CCC in a hole with a 20 amp device and say 12/2 NM. If you are saying that you can then I would definitely disagree. It doesn't matter if the load on every wire is one amp or 20 amps. Enlighten us.Should be ok for 20 amp OCPD if supplying a fixed load that is less than 15 amps. The fixed load will not change no matter what the OCPD is. Which is what I was getting at in my post. 310.15 is about conductor ampacity not overcurrent protection. Many inspectors would see ten cables in the hole(s) and immediately say you can't do that. But there are conditions where you could. They need to question what is going on before jumping to conclusion that it can't be done.