Situation:
New Construction of a large restaurant, building inspector states it's type III-B (??) construction, sprinkled with the kitchen area fire rated construction but the dining areas non-fire rated.
Art 334 allows NM in type III construction except places of occupancy, however, 518,4(B) allows NM where it is non fire rated construction which applies to the dining areas.
The kitchen is fire rated construction but it in itself is not a "place of occupancy"...
Can NM be used throughout the building or would the kitchen walls require metallic ???