I was wandering if what i believe to be rigid metal conduit and an LB body going to pv inverter boxes are a code violation?
I see that there are no support or securing straps withinn 3 feet of box termination or 10 feet for the conduit for every inverteron site.
I do recall that somewhere else in NEC code allows certain sized conduit bodies to be considered supported and secured if RMC is the conduit used but this exemption should no not allow full lengths of RMC to be free standing?
The entire photovaltaic field has all invwrters this way. Do inspectors just overlook these things?
I see that there are no support or securing straps withinn 3 feet of box termination or 10 feet for the conduit for every inverteron site.
I do recall that somewhere else in NEC code allows certain sized conduit bodies to be considered supported and secured if RMC is the conduit used but this exemption should no not allow full lengths of RMC to be free standing?
The entire photovaltaic field has all invwrters this way. Do inspectors just overlook these things?