314.23(E) states if you have raceway entering not more than 300cu inches enclosure (e.g. 4" conduit Tee fitting), the Tee can be supported via the exception as long as two or more conduits that can be threaded into hubs on the Tee - the Tee must same trade size as the largest conduit entry. For example a 2" Tee with a 2" RMC conduit on one side needs only to be supported once, within 3'-5'. There is no need to support the Tee on all three sides within 3'-5'. 344.30(B) would then apply in other words the 2" RMC could be supported at 16'.