Yes but each run of conduit must be supported within 3ft of the box or conduit body. Period. Regardless of what it's going into. It's a requirement to support the conduit, not the conduit body. And there are no exceptions.
I'll add one clarification: if not all three entries of the tee are used and one is just plugged, then supporting the tee with only two conduits is fine.
Looking back, the way the question is phrased is actually moot and misleading and has led to an unnecessarily long thread. Do you have to support the Tee on all three sides? Who cares!? You have to support the conduit anyway, regardless of what it's entering.