344.30 supporting T condulets

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Conduit bodies have no means to attach them to anything. How would one mount it to the structure drill holes in it?
Looking again, the exception appears to apply only to the 100 cubic inches restriction. i.e. a box over 100 cubic inches cannot be supported by conduit, but a conduit body can. Apparently you need a 2.5" conduit body before this even becomes an issue.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Looking again, the exception appears to apply only to the 100 cubic inches restriction. i.e. a box over 100 cubic inches cannot be supported by conduit, but a conduit body can. Apparently you need a 2.5" conduit body before this even becomes an issue.

So going back to post #15; do we need to support a T fitting with 3 conduit entries on all three sides AND within 3’?(no reducers)


Sent from my iPhone using Tapatalk
 