First time I worked with large Aluminum I was like “where has this been all my life”. Its night and day compared to copper installation.

JJ
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
supply house closed. does anyone know how much per foot? its for 320 amp service. thanx

its to feed (2) 150 amp main breakers


Two 150 amp panels is a 300 amp service. Is this what you have?

350mcm is good for 250 amps which is more than you need. For a 300 amp service you only need to use 3/0 aluminum-- 155 amps. I am confused:-?
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Fill in your location (Profile page, shows up on the top left when you post), it will matter where in America you are at.
 

ceb58

Senior Member
Location
Raeford, NC
Two 150 amp panels is a 300 amp service. Is this what you have?

350mcm is good for 250 amps which is more than you need. For a 300 amp service you only need to use 3/0 aluminum-- 155 amps. I am confused:-?

Are you not looking in the wrong column?

If he is referring to the 320amp services I am use to. He would need 4/0 alum. 150amps. 60 deg column
 