supply house closed. does anyone know how much per foot? its for 320 amp service. thanx
supply house closed. does anyone know how much per foot? its for 320 amp service. thanx
Is that code compliant?
First time I worked with large Aluminum I was like ?where has this been all my life?. Its night and day compared to copper installation.
JJ
i have 1.90 so far.
Then you can buy 1 foot.
Is there a but? to this statement
supply house closed. does anyone know how much per foot? its for 320 amp service. thanx
its to feed (2) 150 amp main breakers
Two 150 amp panels is a 300 amp service. Is this what you have?
350mcm is good for 250 amps which is more than you need. For a 300 amp service you only need to use 3/0 aluminum-- 155 amps. I am confused:-?
Are you not looking in the wrong column?
If he is referring to the 320amp services I am use to. He would need 4/0 alum. 150amps. 60 deg column
Why 60C-----?Are you not looking in the wrong column?
If he is referring to the 320amp services I am use to. He would need 4/0 alum. 150amps. 60 deg column