You are thinking 2 conductors per phase, he is not.
Then how does 350mcm aluminum work on 300 amps.
You are thinking 2 conductors per phase, he is not.
You are thinking 2 conductors per phase, he is not.
its to feed (2) 150 amp main breakers
Dennis I was assuming se cable. And we know what happens when we ass u me.
(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334.
FPN: See 310.10 for temperature limitation of conductors.
(b) Exterior Installations. In addition to the provisions of this article, service-entrance cable used for feeders or branch circuits, where installed as exterior wiring, shall be installed in accordance with Part I of Article 225. The cable shall be supported in accordance with 334.30. Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340.
ok here it is . the customer only requires a 200 amp service. he's got big plans. so he says. he insist on 320amp
so thats what he's getting. how about i do this 1.- over head service . pvc down to 320 A single phase meter. I'll get three wire cuts. 2.- install (2) 200 amp 3R disconnects on each side . (they must be outside in this situation) 3.- run 4/0 ser to (2) 200 amp main lug panels. Now, can I use 350 mcm aluminum as my service drop conductors. (1 wire per Phase) ?
Now, can I use 350 mcm aluminum as my service drop conductors. (1 wire per Phase) ?
Dennis,
Table 310.15(B)(6) rates 350mcm Alum. for 300amps @ 120/240 vac 3 wire single phase.
I was wondering where the 300a was coming from in the OP, there it is.