ceb58 Senior Member Location Raeford, NC Mar 18, 2008 #1 Would '08 352.44 for expansion fittings apply to pvc conduit that is being buried and concrete encased? Conduit would be 2 runs of 4" about 100 ft.
Would '08 352.44 for expansion fittings apply to pvc conduit that is being buried and concrete encased? Conduit would be 2 runs of 4" about 100 ft.
resistance Senior Member Location WA Mar 18, 2008 #2 Not much changed from the 2005 to the 2008 on expansion fittings for PVC. I say no!
BackInTheHabit Senior Member Location Lexington, Kentucky Mar 18, 2008 #3 ceb58 said: Would '08 352.44 for expansion fittings apply to pvc conduit that is being buried and concrete encased? Conduit would be 2 runs of 4" about 100 ft. Click to expand... I don't believe it would. 2008 NEC 342.42(A) "Threadless couplings.... Where buried in masonry or concrete, they shall be the concretetight type." Even if the copupling would be concrete rated, I don't the PVC is.
ceb58 said: Would '08 352.44 for expansion fittings apply to pvc conduit that is being buried and concrete encased? Conduit would be 2 runs of 4" about 100 ft. Click to expand... I don't believe it would. 2008 NEC 342.42(A) "Threadless couplings.... Where buried in masonry or concrete, they shall be the concretetight type." Even if the copupling would be concrete rated, I don't the PVC is.