Is it a code violation to add another wire to an overhead ACSR run? And if not what would be your wire selection use or xhhw?
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
Conductors in Parallel

Conductors in Parallel

The parallel cable shall conform with NEC 2014 Art.310.10 Uses Permitted.(H) Conductors in Parallel. (2) Conductor and Installation Characteristics. (2) Consist of the same conductor material.
The ACSR conductor is not specifically recognized in NEC and has to be insulated, in my opinion.
See art. 310.106 Conductors.(D) Insulated. Conductors, not specifically permitted elsewhere in this Code to be covered or bare, shall be insulated.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The parallel cable shall conform with NEC 2014 Art.310.10 Uses Permitted.(H) Conductors in Parallel. (2) Conductor and Installation Characteristics. (2) Consist of the same conductor material.
The ACSR conductor is not specifically recognized in NEC and has to be insulated, in my opinion.
See art. 310.106 Conductors.(D) Insulated. Conductors, not specifically permitted elsewhere in this Code to be covered or bare, shall be insulated.

adding a conductor may not necessarily be paralleling one but the points concerning ACSR valid, however, if the ACSR was allowed in the 1st place, the added conductor might be also.
Ive seen it done with a lot of "W" and "sunlight resistant" conductors.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is it a code violation to add another wire to an overhead ACSR run? And if not what would be your wire selection use or xhhw?
If the additional conductor is part of the same circuit as the original ACSR run, then you have a violation of 300.3(B).
 