I recalled this explanation from Kohler web site, The red mark is done by me,Now let’s see what happens if there is a ground
fault at point A in Figure 4. The current will leave
at point A, it needs to find a way back to the
generator (along the neutral). Its only option is to flow along the ground and to get back into the system at the neutral-to-ground bond at the
service entrance (shown at point B).
Once back in the system, the ground-fault current
will flow along the neutral, through the solid
neutral in the ATS, back to the generator. Just like
during normal current flow, the algebraic sum of
the current through the generator’s ground-fault
sensor equals zero. This means that the ground
fault is not being picked up by the ground-fault
sensor on the generator. The ground-fault sensor
in a generator is often integrated into the circuit
breaker, so in this case the breaker will not open
during a ground fault. In fact, the ground fault may
not be correctly sensed by the system until the
ATS returns to utility power. (It might be seen at
the normal-source breaker, causing the breaker
to trip,
My first question is"why there is no current will flow in the EGC even the generator neutral is not bonded?"
Second question "why still the algebraic sum of the current through the generator’s ground-fault sensor equals zero despite of the presence of ground fault?"