I would not plug thousands of dollars of servers and POS into a $900 generator.
This genset is only 900.00 and is something they had. I haven’t looked into pricing anything for a 3phase system...
They won’t be plugged into genset directly. they will be in a sub panel that is fed by genset. Why wouldn’t you? Actually curious not being a smart a...
Yes sever wise everything is plugged into apc Schnieder battery back ups...
Are the APC SmartUPS or APC BackUPS, huge difference between the product lines. The SmartUPS are generally much better units (and cost more), I won't use the BackUPS except to keep a light bulb lit or maybe a small fan turning.
As for the generator output- that's the whole purpose of the UPS, to make bad power better, and really, even the cheap generators aren't that bad unless they've been badly abused. You don't need crystal-governed generators, here. And there's very little to be lost by doing a controlled test, which I would do anyway.
Yes, generally line-interactive; not as good as Liebert full on-line, but pretty good.smartups are generally line interactive (unless specifically one of the handful of online models)
a) evidence, please (I suspect the generator would need to be having a lot of problems to cause this).they will constantly cycle between line and battery when running on a small construction generator.
Which is exactly what it sounds like.oversize the generator 3x-5x.
from https://www.apc.com/us/en/faqs/FA158891/a) evidence, please (I suspect the generator would need to be having a lot of problems to cause this).
well .. Not sure which is more cost effective or practical,Really what they were worried most about is servers and pos...
I had that issue on one install, the job was sold by another contractor, but they could not fullfill the install schedule (about 100 installs for a big box chain) 12 Kw Generac, the customer ran a business out of his basement, had a large server and UPS, with six workstations. UPS did not like the generator!from https://www.apc.com/us/en/faqs/FA158891/
A common characteristic of generators is the normal output voltage distortion when supplying power to nonlinear loads such as computers. This output voltage distortion can be interpreted by the UPS as unacceptable power quality, forcing the UPS to transfer to battery operation. When the load is transferred to the battery, naturally the generator distortion will be reduced or disappear, leading the UPS to attempt to transfer back to line operation. When the load is reapplied to the generator, the distortion will return, leading the UPS to once again transfer to battery. This cycle may repeat indefinitely at intervals of approximately 4 seconds. The answer in this case is to choose a generator which will not distort, when the nonlinear computer load is applied.
Sorry corrections made... I should use a switched neutral double throw it will be considered a separately derived system and I will need to make sure grounded conductor snd egc at the genset frame are bonded and isolated at sub panel and double throw?
I have a 400a mpd that feeds 3 separate individual 200a breakers and panels. They want a generator installed on one of the panels so they can run there point of sale and server. They’re looking st getting a 10kw 120/240 portable generator. I was going to add a 1ph 200a double throw after the service disconnect and before the 200a panel, but then realized the service is 120/208y 3phase and the generator is only 1 phase... does anyone see that being an issue besides the third phase not having power during an outage or any other concerns? There are no 3 phase loads in the panel being used. All that will be needed during an outages are 7 20amp 1ph 120v circuits 4 for point of sale computers that were pulling 1amp each, and three for servers that were pulling 1.3a, 1.3a, and .9a and three 120v 1 ph 20amp circuits. Any and all help is appreciate! Thanks in advance!