He said the motor would immediately trip the breaker so he was probably taking the unloaded voltage. You're measuring voltage with a 10,000kohm load when you use a multimeter which makes it prone to picking up ghost voltage. 6W holiday incandescent lamp will draw 0.05A or has an impedance of 2.4kohm when lit up. This draws 4,000 times more amps from the circuit than a multimeteIt does exactly the same thing LoZ does. The affected leg won't light up or will be dim or flicker. If it does manage to light up normally without the motor connected, the affected leg will drop out when it is repeated with the motor present.
Filament light bulb is a PTC that has about a 10:1 ratio and it's a simple but a useful instrument because it responds quickly to power glitches. Usually the very first power related issue is flicker. Industrial motor circuits don't share power with lights but when you hook up a power quality meter and press "flicker" it will let you see the same thing you see by hooking up three light bulbs, but they can still have issues with phantom voltage.
Power quality meter is more convenient to hookup and can capture something that happens when you're not there. You certainly won't have to rig up 12v controls transformers connected to some brake lamps nor do you have to worry about those hot light bulbs burning you.
A lot of typing, little result.