250.66 looks to be for GEC not SSBJThat's a good point ! In all likelihood it would not be since its' sized 250.122 and the SSBJ is 250.66.
250.66 looks to be for GEC not SSBJThat's a good point ! In all likelihood it would not be since its' sized 250.122 and the SSBJ is 250.66.
Would this be on the feeder to the trailer?No they just denied the use. they want us to use MC cable and splice to SER when we penetrate the wall going outside.
So let's see if we have this straight. You're going from the transformer secondary to 3 disconnects with 3 runs of MC cable. The disco's are near the transformer. From the load side of the disco's you're running MC cable to the exterior wall of the building where you will transition to SER cable to run to the trailer panel.No they just denied the use. they want us to use MC cable and splice to SER when we penetrate the wall going outside.
Yes, the disconnects are exterior and will feed the trailer panels. Breaker panel are insane lead times right now.So let's see if we have this straight. You're going from the transformer secondary to 3 disconnects with 3 runs of MC cable. The disco's are near the transformer. From the load side of the disco's you're running MC cable to the exterior wall of the building where you will transition to SER cable to run to the trailer panel.
Where are the disconnects located?Here's apic I drew before they shot down the SER inside. Again the splice box will be on wall before we go outside.
The pink is what I just drew in as we're required to use MC inside. Pretty bad pic, I know.
On the other side of the wall. Not in site of the xfrmr. Is that a problem? THere is a door right next to the disconnect that if you open the door you can see the xfrmr? I hope not as I'll be screwed because I submitted my price and it was accepted.Where are the disconnects located?
The secondary conductors are limited in length by 240.21 so how far away are the disco's? Since this is temporary it probably won't be inspected correct?On the other side of the wall. Not in site of the xfrmr. Is that a problem? THere is a door right next to the disconnect that if you open the door you can see the xfrmr? I hope not as I'll be screwed because I submitted my price and it was accepted.
It won't, correct. The secondary conductors will be no more than 100'The secondary conductors are limited in length by 240.21 so how far away are the disco's? Since this is temporary it probably won't be inspected correct?
See post #31...It won't, correct. The secondary conductors will be no more than 100'
???See post #31...
Yes the install is very straightforward but I do want to have the materials ready for when they get onsite.I think you are too concerned about the details and lack the field experience. I would think you best bet would be to sketch a oe-line, order the transformer and disconencts and turn the job over to a qualified journeyman. It, should be a fairly routine install for an experienced electrician.
I hear you but the panels was almost $6k and a lead time of 3-4 weeks. The disconnects were $900 and in stock.Just my 2 cents but it seems to me that your initial plan of feeding a panel from the transformer with the panel right next to it was a better choice. Since your labor costs are very high running 3 sets of secondary conductors to 3 separate fused disconnect switches that have to be mounted and wired doesn't seem like you saved any money. A panel would have been less work, cleaner, and would leave some room for expansion down then road if needed.
That's a big number so you're right that the disco's are a better option. Even the slowest electrician probably won't eat up the extra $5K.I hear you but the panels was almost $6k and a lead time of 3-4 weeks. The disconnects were $900 and in stock.
That's a big number so you're right that the disco's are a better option. Even the slowest electrician probably won't eat up the extra $5K.![]()