Does the 83% rule for dwellings (310.15(B)(7)) apply to a subpanel being fed off the service panel? In this case we have a 200A MSP and a branch to an Enphase Enpower smart switch panel and a branch from the smart switch panel to a backed up loads panel. The contractor proposes to protect both panels with 200A breakers. He proposes to use 4/0 Al SER conductors having 180A rating.
For the MSP - smart switch circuit it seems to me the maximum current would be the same as the 83% of the service conductors, 166A, so 4/0 Al SER would work. But these conductors are branch conductors, not service conductors, so would the 83% rule apply?
For the smart switch - BU panel there would be additional power sources from the PV and battery, so I think we need to use a smaller breaker.
For the MSP - smart switch circuit it seems to me the maximum current would be the same as the 83% of the service conductors, 166A, so 4/0 Al SER would work. But these conductors are branch conductors, not service conductors, so would the 83% rule apply?
For the smart switch - BU panel there would be additional power sources from the PV and battery, so I think we need to use a smaller breaker.