Re: 4/0 cable into the back of a 3 1/2 inch deep panel
Pierre thank you for pursuing this with Square D, I knew you would present the info without a predetermined agenda, and also that you would report your findings back whatever the outcome.
Everyone,.. first we are not talking about distances to terminals, we are taking about the bending space between the back and front of a 3.5" deep enclosure, call it a panel, gutter conduit body, whatever you want but it must comply with Table 312.6(A) Minimum Wire-Bending Space at Terminals
and Minimum Width of Wiring Gutters
Take a look at 314.28(A)(2) (posted below) to see an example of this for LBs and would apply to the panel as the panel front is removable.
The space from the terminals is determined as a separate issue.
I still do not understand a couple of the augments presented here that are in support of allowing 4/0 in the back of a 3.5" deep box.
1)They would not put a 2" KO in the back if it was against code to use it.
Say what? :roll:
2)LBs or conduit bodies if you want.
As I pointed out earlier.
They are stamped with the max conductor size and quantity, this amount will be less than what the raceway they are connected to can accommodate.
And the code Don was kind enough to point out.
314.28(A)(2) Angle or U Pulls. Where splices or where angle or U pulls are made, the distance between each raceway entry inside the box and the opposite wall of the box shall not be less than six times the metric designator (trade size) of the largest raceway in a row. This distance shall be increased for additional entries by the amount of the sum of the diameters of all other raceway entries in the same row on the same wall of the box. Each row shall be calculated individually, and the single row that provides the maximum distance shall be used.
Exception: Where a raceway or cable entry is in the wall of a box or conduit body opposite a removable cover, the distance from that wall to the cover shall be permitted to comply with the distance required for one wire per terminal in Table 312.6(A).
Our we all yet in agreement that there is not sufficient space to enter 4/0 conductors in a enclosure that the opposing wall of is less than 4" away?