4 - 20 mA read in parallel

Status
Not open for further replies.

Besoeker

Senior Member
Location
UK
The original poster said that the meter was set for current, not voltage.

One of the advantages of reading the voltage drop across the input resistor is that you don't have to open the circuit to take the reading. Yes, it will have, as you said some impact on the reading, but not much and not near as much as if you set the meter to current and put it across the input terminals.
I agree. I too,have seen a 250ohm resistor used in the equipment being fed by the 4-20mA source. A multimeter on a voltage range is probably going to have an input impedance in the meg ohm range. It's loading effects would be negligible.

I don't think the following has been mentioned yet.
Another reason for using 4-20mA signals is that it is fairly immune to noise. And, within reason, the length of run doesn't affect the signal value. As a current source the sending end voltage will adjust to compensate for voltage drop.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
Another reason for using 4-20mA signals is that it is fairly immune to noise. And, within reason, the length of run doesn't affect the signal value. As a current source the sending end voltage will adjust to compensate for voltage drop.
I agree. Current is what is important in this circuit. If the sending end sees current is too low for the conditions it likely raises voltage in order to raise current, the receiving end shouldn't care much about voltage, it is current it is analyzing for deciding what to do next.
 
Status
Not open for further replies.