As Jim Dungar said, 110VDC is the bugaboo here. You may technically be able to use the typical 30mm industrial control pilot device type switches (if you can find them in 5 position), but switching DC is more difficult than AC so their contacts are usually limited to very low DC energy capacity, as in 50-80VA max. That means roughly 450-730mA at 110VDC. Allen Bradley's for example are limited to 69VA, so 630mA and if you are switching anything with a solenoid it will not likely take it. Those Square D cam switches are not rated for using on DC at all! So make sure you check any options out thoroughly before using them on 110VDC.
Look at the Electroswitch devices for the Power Industry, i.e. Switchboard cam switches. They are much bigger and have more DC capacity.