OK let's do this.
There is no reduction
allowed after the lighting appliance branch-circuit panel(s).
This article specifically allows reduction to the first lighting appliance
branch-circuit panel(s) down line of the service equipment.
Lets walk through this. We will use a lateral in this example
400A service
2-200 amp lighting appliance branch-circuit panels.
Service lateral --400KCM copper per article 310.15(b)(6) to 400A OCPD.
We still have not made it to our lighting appliance branch-circuit panels
yet.
For sake of coversation we install 2-200 amp enclosed breakers adjacent to
this 400 amp OCPD and feed these from parallel lugs.
We use 2/0 copper per 310.15(b)(6).
We still have not made it to our lighting appliance branch-circuit panels
yet.
We feed 2-200 amp lighting appliance branch-circuit panels with 2/0 copper
per 310.15(b)(6)and make all terminations.
We have finally made it to our lighting appliance branch-circuit panels.
Now 310.15(b)(6) has seen it's end and if we feed any sub panel, say a 100 amp, from one of these aforementioned lighting appliance branch-circuit
panels, this 100 amp sub panel can not use 310.15(b)(6)
Roger