jrmac

Member
I am looking for a 3conductor with ground #4 copper wire in an outer jacket. Probably a THHN type. Is such a thing available? I am adding a 100 amp subpanel in the basement of my home. I want to run this wire about 40 feet. Help
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: #4 copper wire

Yes, you can buy #4 "3 conductor with ground" cables in NM, SER, MC etc... but the #4 is not large enough for a 100 amp panel downstream of your Main lighting and appliance branch circuit panel.

You will have to use #3 with a 75 deg C listing for this or protect this new panel at a lower amperage.

Roger

[ January 01, 2004, 10:04 PM: Message edited by: roger ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: #4 copper wire

John Mac, you are welcome. Be aware that some will tell you the #4 could be used under article 310.15(B)(6), but in this case it isn't applicable.

Roger
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: #4 copper wire

Speedypetey

310.15(B)(6) only allows the conductor sizes shown in table 310.15(B)(6) for the main power feeder to a dwelling. The feeder in question is not considered the main power feeder.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: #4 copper wire

Just above Table 310.15(B)(6) is section 310.15(B)(6) part of which says:

For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboard(s).
 

pierre

Senior Member
Re: #4 copper wire

Any panel that is past (downstream) of the first lighting and appliance branch-circuit panel in a dwelling is not permitted to use the table 310.15(B)(6). Also that table does not have NM cable (most widely known as Romex)as one of the permitted types of conductor/cable types.

Example:
A service disconnect (located immediately inside or outside the dwelling) feeds the main panel in a dwelling, that is one example of a main power feeder as per NEC.

Supplying a panel from the main panel in a dwelling, the feeders supplying the second panel are not considered main power feeders and one cannot use table 310.15(B)(6).

Pierre
 

bennie

Esteemed Member
Re: #4 copper wire

There is no such thing as a subpanel. Therefore there is no feeder for a sub-panel.

Table 310.15.B.6 Is titled; Conductor types and sizes for Single phase Dwelling Services and Feeders.

No feeder is required to be larger than the service entrance conductors.

All supply conductors to dwelling panels are included in the Table 310.15.B.6.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: #4 copper wire

Bennie you should read the section in question before saying the table applies to all dwelling unit feeders.

We do not even have to go down the sub panel route to figure out what the table applies to.

Part of section 310.15(B)(6)
For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboard(s).
No mention of a sub panel but still clear this table is only for main feeders.

[ January 02, 2004, 09:54 AM: Message edited by: iwire ]
 

bennie

Esteemed Member
Re: #4 copper wire

Bob: All dwelling panels are lighting and power panels. The supply to each one is the main power feeder.

Read the paragraph below the one about main power feeders in 250.15.B.6. This is saying that no feeder is required to be larger than the service conductors.

I maintain that the feeders to all lighting and power panels, in a dwelling, are main service conductors. A service is the equipment for delivering electrical energy from the serving utility to the wiring system of the premises served.

Service equipment is not a component of the premises wiring system.

I don't care if anyone agrees with me, but put some thought in my statements, and when trashing me please quote documents to substantiate a different perception.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: #4 copper wire

Bennie:
"No feeder is required to be larger than the service entrance conductors."
The NEC clearly only allows the increased ampacity to apply to the main power feeder as Pierre states. This issue has been changed in the last few code cycles and its intent is now clear. In some cases the feeder may be larger than the service conductors.
 

bennie

Esteemed Member
Re: #4 copper wire

Tom: I'm reading from the 2002 Edition. Where does it say that the reduced ampacity does not apply to feeders to all panels in a dwelling?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: #4 copper wire

Bennie I did provide a document to substantiate a different perception.

I provided it from the only source that means anything when speaking of NEC rules, the NEC itself.

I am sorry you feel like you are getting trashed, that is what can happen when you intentionally go against the flow.

I respect those that do go against the flow and question things, but if choose to do this you must develop a thick skin. :)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: #4 copper wire

Here is my explanation, and I'm sure some are tired of reading it. :D

rp.deas@verizon.net
unregistered


posted December 20, 2002 10:38 PM
--------------------------------------------------------------------------------
OK let's do this.
There is no reduction
allowed after the lighting appliance branch-circuit panel(s).

This article specifically allows reduction to the first lighting appliance
branch-circuit panel(s) down line of the service equipment.


Lets walk through this. We will use a lateral in this example

400A service
2-200 amp lighting appliance branch-circuit panels.

Service lateral --400KCM copper per article 310.15(b)(6) to 400A OCPD.

We still have not made it to our lighting appliance branch-circuit panels
yet.


For sake of coversation we install 2-200 amp enclosed breakers adjacent to
this 400 amp OCPD and feed these from parallel lugs.

We use 2/0 copper per 310.15(b)(6).

We still have not made it to our lighting appliance branch-circuit panels
yet.


We feed 2-200 amp lighting appliance branch-circuit panels with 2/0 copper
per 310.15(b)(6)and make all terminations.

We have finally made it to our lighting appliance branch-circuit panels.

Now 310.15(b)(6) has seen it's end and if we feed any sub panel, say a 100 amp, from one of these aforementioned lighting appliance branch-circuit
panels, this 100 amp sub panel can not use 310.15(b)(6)

Roger
Roger
 

bennie

Esteemed Member
Re: #4 copper wire

What part of " The feeder conductors to a dwelling unit shall not be required to be larger than their service entrance conductors, am I missing?
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: #4 copper wire

Maybe there are two of us that do not understand 310.15(B)(6).

"For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch circuit panelboard(s)".

Between the main disconnect--- Wouldn't the main breaker in a 200amp panel be the main disconnect?

If so a panelboard after this would be fed by a main power feeder, per the definition stated in 310.15(B)(6).

While I do not have the knowledge of some of the posters, I do have an excellent understanding of the English language.

If there were no main (disconnect)in the first panel I would understand that Table 310.15(B)(6) does not apply.

Mike P.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: #4 copper wire

Mike Think of a combination Meter socket Main breaker combo outside, inside a 200 amp MLO or main breaker panel.

The conductors from outside to inside would be the main feeders.

Any feeder down line from that first indoor panel will not be a main feeder.

If you killed the power to this second feeder you would still have power at the first panel, so it is not a "main"
 

earlydean

Senior Member
Re: #4 copper wire

Bennie,
The key phrase is "The feeder conductors TO a dwelling unit" Implying that there is only one feeder to this dwelling unit. This is made abundantly clear in the NEC Handbook. The first disconnect may be called a "power panel", where the main panel in each apartment is the "lighting and appliance" panel. The feeder from the main disconnect to the main panel is allowed to be sized per 310.15B6, while any other "sub-panels" fed from the main panel, would not be able to be sized using 310.15B6. Such "sub-panels" are fed FROM the dwelling unit, not TO the dwelling unit.

You are right in saying there is no such thing as a "sub-panel" (except those installed in a submarine). All panels are classified as either a power or a lighting and appliance branch-circuit panelboard (408.14). But we all know that it is commonly understood that all panels other than service or separately derived panels are sub-panels.
 