#4 copper wire

Status
Not open for further replies.

bennie

Esteemed Member
Re: #4 copper wire

Ever since I have been doing electrical work, I have never heard of larger wire at the end of a circuit. This is ludicrous and insults my intelligence.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: #4 copper wire

Bennie, I've got to ask, where would we feed a downstream panel from another panel at the same capacity, and if we were to do so, why wouldn't we just size one feeder to accomodate both panels the way I explained it?

Roger
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: #4 copper wire

"The key phrase is "The feeder conductors TO a dwelling unit" Implying that there is only one feeder to this dwelling unit."

If this is true please explain the reference to feeder(s) later in this section. This is what I am having a problem with not the first half.

Mike P.
 

bennie

Esteemed Member
Re: #4 copper wire

Roger: I'm not clear on what you ask.

Service entrance conductors and feeder conductors are determined according to the load.

A second panel supplied by the first panel will not have a higher calculated load than the service panel. Why have No #4 for the service and #3 for the second panel?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: #4 copper wire

Bennie, this is my point exactly, why would we have a 100 amp downstream panel fed from another 100 amp panel?


Roger
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: #4 copper wire

Part of 310.15(B)(6)
The feeder conductors to a dwelling unit shall not be required to be larger than their service-entrance conductors.
So if we are talking about the service conductors they will never be required to be larger that the feeder.

The one place that could be odd would be 100 amp service disconnect outside use 4 awg from the outside service disconnect to the first panel.

Now if we add a 100 amp panel down stream from that first panel we would have to run 3 AWG.

But

1) When do you in a dwelling unit add a second panel of the same capacity as the first.

2)You could put two service disconnects outside and run 4 awg from each to panels inside.
 

bennie

Esteemed Member
Re: #4 copper wire

Roger: A better example is a 200 amp service panel and a 100 amp panel fed from the service panel. The second panel should be supplied by No. #4, it is a feeder. Many are going to say the Table 250.15 does not apply.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: #4 copper wire

Bennie, no argument that this is a feeder, but it is not a "Main Power Feeder" as defined in 310.15(B)(6). This is the sole reason we can not apply this article section to this (for lack of an NEC term) "Secondary Feeder".

If the section was to allow derating of all feeders it would not have had to waste the ink on text in 310.15(B)(6), the table could have stood alone.

Roger
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: #4 copper wire

"Many are going to say the Table 250.15 does not apply."

I think it does. I want to know why I am wrong.

Again the "between" is my problem. Please explain to me why a feeder "from" the disconnect does not use the table.

Mike P.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: #4 copper wire

In my opinion the table in question can be used for all lighting and appliance branch circuit panels in the dwelling. Look at the definition of "main power feeder" in this section. All feeders to panels meet the requirements of the definition. While the words "main power feeder" strongly implies that this feeder feeds all of the loads in the dwelling unit, there is nothing in the definition that supports this. The definition only has two conditions, 1) that the feeder supply a lighting and appliance branch circuit panel and 2) that the feeder originates on the load side of the service disconnect.
Don
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: #4 copper wire

OK I give, :eek: I am sorry Bennie, Don's post made me look at it in a different light. :eek:

Looking at the way it's worded the feeder to a "sub panel" is still in between the service disconnect and the panel.

Bob
 
A

a.wayne3@verizon.net

Guest
Re: #4 copper wire

Roger at first I looked at this post and said huh...But you are right as soon as you terminate in your panel any panels after that can`t go by that table anymore.See we all learn something each and every day.That`s why I keep coming back here thanks guys
Allen
 

bennie

Esteemed Member
Re: #4 copper wire

I don't want to create another controversy at this time, but will later on when I describe my reason for concluding all residential panels are service panels, and should be treated as such.

A commercial panel is different due to the feeder usually being installed in a metal conduit. This makes it necessary to take means for preventing parallel load current from flowing on the conduit.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: #4 copper wire

Bennie

"I don't want to create another controversy at this time"

I want you to. You and others have made me think like (as) I never have before.

Mike P.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: #4 copper wire

Don, you stated in your post that it was your opinion that 310.15(B)(6) could be used for all the feeders to panels in dwelling units, so what is your stance?

Would you tell John Mac that the #4 can be protected at 100 amps for this downstream panel, or would you tell him he can not protect it at more than 70 amps for 60 deg C, or 90 amps for 75 deg C?

Roger
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: #4 copper wire

Originally posted by bennie:
Ever since I have been doing electrical work, I have never heard of larger wire at the end of a circuit. This is ludicrous and insults my intelligence.
Bennie with all respect; what if VD is the issue and not current, and your to cheap to buy a transformer?
 

bennie

Esteemed Member
Re: #4 copper wire

Large wire at the end of a circuit is too late for voltage drop prevention. The voltage will already be lost trying to get to the big wire.
 

speedypetey

Senior Member
Re: #4 copper wire

Originally posted by jxofaltrds:

I want you to. You and others have made me think like (as) I never have before.

Mike P.
This is why I asked my original question.


I have always considerd any conductors feeding a panel "feeders", as opposed to branch circuit conductors.

Art. 100-
" Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device."

Wouldn't conductors between the service equipment (main panel) and the final overcurrent device (sub-panel, sorry Bennie) be feeders by this definition?
 