https://mart.cummins.com/imagelibrary/data/assetfiles/0056582.pdf
Power topic #6006 | Part 2 of 2 | Technical information from Cummins Power Generation
Grounding of AC generators and
switching the neutral in emergency
and standby power systems
If, and only if, 4-pole transfer switches are used the
generator must be grounded as a separately derived
system.
The generator neutral should not be bonded to
its equipment grounding electrode where the generator
neutral is solidly interconnected with the grounded
neutral of the normal supply, except where switched
neutral transfer equipment is required.