As I wrote before that we are not using any 277V but my boss said first consideration was to conform with NEC Art 250.20B, Art 250.24B & aArt 230.35. He likes to have a separately derived system because our building has many computers and PLCs, so he would like to have our 4th wire conected to the switch. But I have told him that it is the same wire that we used to bond the metal parts of our motors, panels and step-down transformers, thus I believe it is an equipment ground.
Our transfering means is a breaker-type switch, in the event that a line-to-ground fault occurs on the load of the switch it will trip both the normal breaker and not transfer to emergency (because the sensor will detect that there is still power coming from the source) or during maintenance wherein we open both breakers, would that be a hazard because the whole load-side of the switch will not have any connection to ground on these intances? I believe what he wants is applicable only if we have a true nuetral because there would be another wire that will bond all the metal parts of our plant. But as I wrote, we only have a 4th wire that does this.