We have 4 Solis 10k inverters, parrelleled, 4g thhn from inverter to breaker on each inverter. 4/0 aluminum wire runs from combiner box up to disconnect whis is 300 feet. This disconnect is tapped into lines below meter whis is all 4/0. If we power up 2 inverters, they get up to 8000 watts, the line voltage goes up to 258.0 volts at inverters, 252.0 volts at disconnect. If we power 3rd inverter up, voltage ramps up over 264.0 volts and shuts inverter down.
New wire, connections all tight, check line resistance in the 4/0 as well.
If no inverters are turned on, the voltage is 248.0 at both the disconnect and at combiner box at inverters.
Any ideas?