Don't have the book in front of me, do you 4-way switches require a neutral at the switch when using NM cable without future access?
(C) Switches Controlling Lighting Loads. Where switches
control lighting loads supplied by a grounded general purpose
branch circuit, the grounded circuit conductor for the controlled
lighting circuit shall be provided at the switch location.
Exception: The grounded circuit conductor shall be permitted
to be omitted from the switch enclosure where either
of the following conditions in (1) or (2) apply:
(1) Conductors for switches controlling lighting loads enter
the box through a raceway. The raceway shall have
suffıcient cross-sectional area to accommodate the extension
of the grounded circuit conductor of the lighting
circuit to the switch location whether or not the
conductors in the raceway are required to be increased
in size to comply with 310.15(B)(3)(a).
(2) Cable assemblies for switches controlling lighting
loads enter the box through a framing cavity that is
open at the top or bottom on the same floor level, or
through a wall, floor, or ceiling that is unfinished on
one side.
(C) Switches Controlling Lighting Loads. The grounded
circuit conductor for the controlled lighting circuit shall be
provided at the location where switches control lighting
loads that are supplied by a grounded general-purpose
branch circuit for other than the following:
(1) Where conductors enter the box enclosing the switch
through a raceway, provided that the raceway is large
enough for all contained conductors, including a
grounded conductor
(2) Where the box enclosing the switch is accessible for
the installation of an additional or replacement cable
without removing finish materials
(3) Where snap switches with integral enclosures comply
with 300.15(E)
(4) Where a switch does not serve a habitable room or
bathroom
(5) Where multiple switch locations control the same lighting
load such that the entire floor area of the room or
space is visible from the single or combined switch
locations
(6) Where lighting in the area is controlled by automatic
means
(7) Where a switch controls a receptacle load
Is it true this requirement has to do with facilitating occupancy sensors?
Which would not require an unobstructed view of the area covered.Yes and any other control that might be installed like a time clock switch.
Which would not require an unobstructed view of the area covered.
How many of those automatic controls were replacing a three way or four way switch and leaving the original switching scheme as it was?Maybe I want to see the time clock from anywhere.
Of course you are right about that yet still the code section was added to address any switch box mounted device that was using the EGC as a circuit conductor as many occ sensors and time clocks did.
How many of those automatic controls were replacing a three way or four way switch and leaving the original switching scheme as it was?
I though it would be more then that183,266.974211
I though it would be more then that
How many of those automatic controls were replacing a three way or four way switch and leaving the original switching scheme as it was?
I guess that was indirectly part of my previous question. Even three ways can be a little questionable. If you get multi-sensor/switch systems, how many of them use the three/four way traveler conductors in same manner as a typical set of toggle switches does? Many I believe are a master/slave system where you don't even need direct wiring between the master/slaves.Has anyone ever seen a device that could replace the 4-way switch?
I guess that was indirectly part of my previous question. Even three ways can be a little questionable. If you get multi-sensor/switch systems, how many of them use the three/four way traveler conductors in same manner as a typical set of toggle switches does? Many I believe are a master/slave system where you don't even need direct wiring between the master/slaves.
If you put multiple "single pole" occupancy sensors in place of a three/four way switching scheme, so that they are in parallel to one another you free up a conductor (hopefully a white conductor) that can be used as a neutral for powering the device, four way switches can still be tricky depending on how wiring was run.
My opinion? - NO. Code requirement? - IDK, is not all that clear.So after all of that is the neutral required at the 4-way switch say for a stair case or multiple rooms?
My opinion? - NO. Code requirement? - IDK, is not all that clear.
I think this is a design issue and shouldn't be a code rule in the first place.
So after all of that is the neutral required at the 4-way switch say for a stair case or multiple rooms?
How about making it illegal to use the EGC for a grounded conductor for the manufacturers?