I'm from the UK and I read this topic with a .... fascination!
If I understand the topic correctly you are removing the 4 core lead (L1, L2, N & E ?) & reconnecting a 3 core lead (L1, L2 & E ?) by connecting together the neutral & ground in the dryer so that a current will deliberately flow along the ground wire since there is no neutral available?
I understand why this will work (and that you common the neutral & ground at the service entrance) but for me it seems so .... strange.... our wiring regulations absolutely forbid the use of an egc as a 'normal' current carrying conductor under any circumstances.......
or have I mis-understood?
(I'm not questioning the rules - the rules are different Country by Country... just merely trying to increase my knowledge of electrical system in other parts of the world)
A valid question, and without the historical background it is quite understandable.
The premise is not replacing an existing four wire cord with a three wire cord, but rather that fact that at one time it was permitted by NEC to run only a three wire branch circuit wire set for a large appliance like a cooking range or a clothes dryer. This was at the same period that there was no requirement to bring a ground to a normal light or appliance circuit at all.
For the most part loads did not have any grounding of exposed metal parts, but it was considered OK in the case of range or dryer to connect the case to the neutral wire. Both range and dryer would typically have at least one line to neutral load (timer motor, lamp, etc.) in addition to the line-to-line loads, so the neutral would be current carrying. If the dryer motor was 120V or the range elements used a 120 volt connection for low power, the neutral could carry significant current.
The receptacle plug contains only three contacts.
The NEC allows use of a combined neutral/ground wire
in the appliance cord for legacy applications where there are only three conductors in the wall.
What is causing concern in this particular case is that the third wire in the wall is uninsulated (except for the overall sheath), and was landed at the ground bus rather than at the neutral bus of the panel. And there appears to be a problem with the overall ground to neutral bonding to complicate things.
New installations are governed by the same restriction that you cite, namely that the Equipment Grounding Conductor (EGC) not be used to carry normal current.
The only exception there at the moment is for presence detectors or dimming controls in light switches where there is only a switch loop and no neutral at the device box. Which is another can of worms....