Is it required by the NEC to have a 4 wire home run for a stove/range? GC is giving a hard time about this subject.
infinity said:Why does the GC care in the first place? Is he the licensed electrical contractor?
Flat out ~ NO.cross1 said:Is it required by the NEC to have a 4 wire home run for a stove/range?
What's his arguement???cross1 said:GC is giving a hard time about this subject.
I'll share something with you that my Nascar-watching father once told me: Second place is simply the first loser.charlie b said:That would have been my answer too, if I had seen the question first. But in a quick attempt to get my post count closer to George's :grin:, let me add that the relevant code article is 250.140.
cross1 said:Is it required by the NEC to have a 4 wire home run for a stove/range? GC is giving a hard time about this subject.
celtic said:Flat out ~ NO.
How about we use Type AC, EMT, RMC, etc and an appropiately sized EGC on the box
(Devil's Advocate).
Let's not assume the world is wired with NM
What's his arguement???
JohnConnolly said:Spinoff question. I have seen SOME cooktops that are staight 240 with NO neutral connection. Are 4 wire NM circuits required in this case?
I don't know if anybody (AHJ) would allow a NEW cooking/drying circuit to be 3-wire. I suppose there are 3-prong cord caps for 4-wire cord,...? But the new wire would, I believe, still have to be 4 conductor.JohnConnolly said:Spinoff #2. Can you use 3 wire NM to RELOCATE a range/oven/dryer circuit? I assume so.
cross1 said:Can you prove by NEC that it doesn't have to be 4 wire. GC questions everything...thinks he knows all codes for all...just a pain.
kdog29 said:I'm getting a hard time from a GC also on condo remodels. He keeps telling me I'm buying too much material. He bids the jobs without consulting an electrician, then freaks out when there's more work or material involved then what he saw in his crystal ball or what was spent on another one.
That is where I was headedeprice said:I don't want to speak for celtic, but I think what he is getting at is that all of the raceways he mentions are listed in 250.118 as being acceptable equipment grounding conductors. If one of those wiring methods is used for the range circuit, you can get by with only 3 wires. The raceway can be the fourth conductor.
cross1 said:Can you prove by NEC that it doesn't have to be 4 wire. GC questions everything...thinks he knows all codes for all...just a pain.
The ONLY way you would you be allowed a 3 wire to the range is under 2 conditions:charlie b said:....the relevant code article is 250.140.
kdog29 said:I'm getting a hard time from a GC also on condo remodels. He keeps telling me I'm buying too much material. He bids the jobs without consulting an electrician, then freaks out when there's more work or material involved then what he saw in his crystal ball or what was spent on another one.