But the 30 Amp disconnect would be protected by the 40 A breaker which is a violation, correct?
The breaker provides only SC and GF protection.
Check out 430.62, 430.24
But the 30 Amp disconnect would be protected by the 40 A breaker which is a violation, correct?
If this is a dwelling unit, then I think 210.23(C) kills the idea.
But the 30 Amp disconnect would be protected by the 40 A breaker which is a violation, correct?
I am aware that motors are not sized in 210:grin:, but this is not a motor found in a paper mill, this is part of a piece of equipment. So where do you draw the line when to size off 430 versus 210. what if you have equipment that has a motor as only one part, but also includes other non motor loads?![]()
422.3 Other Articles.
The requirements of Article 430 shall apply to the installation of motor-operated appliances, and the requirements of Article 440 shall apply to the installation of appliances containing a hermetic refrigerant motor-compressor(s), except as specifically amended in this article.
Can you elaborate on this? You lost me.![]()
If the 30 amp disconnect has a minimum of 40 amp conductor supplying it, no violation.
I am still lost on this, I am sure I am missing something simple here, but isn't the disconnect an extension of the circuit which is protected at 40 amps. Therefore the disconnect could be drawing 39 A through it, burn up because it is not rated for that amount of current and never trip the breaker out. I am planning to pull #8 THHN to the disconnects but it seems like they would need to be 60A disconnects.
It is not going to draw 39 amps for very long if it only has 30 amp or smaller fuses in it. That is why it is there. You have same thing if you have a 400 amp fused switch as a service and then tap lets say 8 fused switches of any rating smaller than 400 amps to supply whatever it is you are working with. The tap conductors will not carry more current than the connected load, but do need to be sized according to tap rules so they are not compromised during a short circuit or ground fault event that happens on the supply side of the tapped disconnect.
A similar situation is in a loadcenter. Say you have a 200 amp main breaker. The busses are protected from short circuits and ground faults by the main breaker @ 200 amps. The buss is the feeder. Now plug in some smaller breakers. The plug on the breaker is the tap connection, inside the case is the overcurrent device for the lower amperage circuit connected to the load side.
Why would you do that-- buy a disconnect that is made for the purpose. By the time you try and do what you say it will cost you a lot more money.
Good point.:grin:
So then I would need to make sure the provisions of 240.21 apply correctly if using a 30 Amp disconnect?
Which after reading 240.21(B)(1), mounting a 30 Amp disconnect on this 40 Amp circuit will meet NEC guidelines.
Thanks for all the help guys.