40 amp dryer circuit

Status
Not open for further replies.
Other than the fact that they ay have used an old range circuit I have no idea why it would be on a 40 amp circuit. 30 amp is what is required.
 
I've also seen 60 amps range circuits and other circuits that are incorrectly protected. If I'm doing a panel change, I automatically correct these situations. Otherwise, I strongly suggest to the HO that they change them to avoid a fire. Just the other day I came across a 20 amp water heater (with #12 wires) on a 30 amp breaker.
 
Actually, in the 50s, there was a dryer that took a 50amp circuit. The concept did not last long, but I think it was to mimic a gas dryer in speed. Someone older may remember it.
 
Not to code, but if you ask me thats a none issue. Common practice in Canada.

:? I don't see how you can say protecting a 20 amp circuit with a 30 amp breaker is a non-issue. Don't we discuss putting the proper sized breaker on circuits all the time.
 
:? I don't see how you can say protecting a 20 amp circuit with a 30 amp breaker is a non-issue. Don't we discuss putting the proper sized breaker on circuits all the time.



The heater isn't a receptacle- more load can not be added to the circuit.
 