The Plan checker has corrected my plans and has stated that I need to provide a main circuit breaker for panel A1,(the secondary panel) per ?240.21, 408.36.
I have a 400 amp service with a 400 amp main breaker it's feeding panel "A", a 400 amp M.L.O. feed thru panel, then it comes off the feed thru double lugs with 400amp wire to panel A1 which is only 5ft away the Plan checker says that per 2410.210(b) it requires me to install a main in panel A1. is this Correct? I am not changing the size of wire anywhere. How should I comment back to him?
Thanks for your suggestions.
I have a 400 amp service with a 400 amp main breaker it's feeding panel "A", a 400 amp M.L.O. feed thru panel, then it comes off the feed thru double lugs with 400amp wire to panel A1 which is only 5ft away the Plan checker says that per 2410.210(b) it requires me to install a main in panel A1. is this Correct? I am not changing the size of wire anywhere. How should I comment back to him?