Is it set up like this?
Utility > 400 amp main > 400 amp conductors > 400 amp MLO 'A' > 400 amp conductors > 400 amp MLO 'A1'[/QUOT]
So, Does it mater where the MOCPD is located? Can it be in the Service Equipment rather then in the first panel "A"?
Again thanks for all the feed back.
Yes, it can be in the service eqpt. My question is, does panel A1 have 400a bus? If not, it would have to be protected for minimum ampacity. For convenience to isolate sub panels, mains are sometimes preferred, not required.