I don?t mean to give you a hard time, but the building has a 400 amp main what? Is there already a meter and a disconnect? If so, that is the point at which the rules for ?service conductors? ends, and from that point to the tenant?s equipment you follow the rules for ?feeder conductors.? If you have a need for 400 amps of highly harmonic loads, then you need at least 500 amps worth of conductor. If you use a 90C rated conductor, you can de-rate from the 90C table. Thus two possible choices are a single 700 MCM or a pair of parallel 4/0. In both cases, the 90C ampacity is 520 amps, and de-rating that to 80% gives you 416 amps.Originally posted by j87: . . . this is a building that has a 400 amp main.
A couple of points just out of curiousity.Originally posted by charlie b:
But back to basics. You say that no load calculation is available? Then you must perform one! The tenant might say they want 400 amps, but they might have 800 amps worth of equipment in the space, just waiting for you to give them the power. If you had not installed a 400 amp feeder on the basis of a known load under 400 amps, then the responsibility for the ensuing fire will come knocking on your front door.
We generally run 500 or 600 Kc mil CU for a service or feeder that has 400 Amp over current protection.Originally posted by petersonra:
Do you guys usually run conductors this large? Or do you prefer multiple smaller conductors in parallel?
It?s an old habit of mine, obtained from an industry that goes out of its way to avoid reliance upon a protective trip as the sole means of preventing an accident. You want the breaker to work, and you fully expect that it would. But you never design a system in such a way that normal operations would frequently overload that breaker, and force it to trip, as the sole means of preventing a fire.Originally posted by petersonra: How could you end up with more then 400A load? presumably the loadcenter being installed has a 400A main that would trip long before a fire hazard came about.
Does not make since if a "K" rated transformer, or a overated panel board is not used. Seriously doubt the utility oversized the neutral.Originally posted by rjdad82:
Most of the time it calls for a 200% neutral or a dedicated neutral for each individual branch circuit.