kwired
Electron manager
 - NE Nebraska
 - EC
I already have but when I was on the phone I couldnt rattle off all of the violations that would come into play other than you cant do that because of this, and this, and this.
The DIY'er said the power company told him they used this setup for 400 Amp services all the time.
You can see where he would think that installing a 400 Amp Panelboard would be just fine.
It was the first time I had ever heard of anyone even thinking about installing it that way.
POCO probably only looks at it as a 400 amp service, which it is and to them does not matter if it is 1 - 400 amp load, 2 200 amp loads, or 75 loads that total 400 amps, but it is not capable of supplying a single 400 amp circuit.
That would make no difference IMO. If one conductor from one of the breakers got cut or disconnected somehow the entire 400 amps would be on the 200 amp conductor and breaker. :happyno::jawdrop:
It does not matter for the fact there is a 400 amp feeder being supplied. If it were supplying two separate panels but on a separate building or structure is where 225.30 issues are a problem.
It only matters if the service is on the building if you were to correct the problem by replacing the single 400 amp panel with 2 200 amp panels because, as Kwire points out, it would violate 225.30. That is why I suggested my fix to change it to a single 400 amp breaker at the meter and it comes a legitimate parallel feeder. But since you are not being called on to fix the obviously wrong and dangerous original design, it's a moot point and case closed. The only thing I would do is issue a letter stating the concerns and hazard so there is a paper trail showing you did your best to make the owner aware and move on.
Not much you can do but notify them that it does not meet codes and standards. I certainly would not be willing to make any change to it without some funds up front or I will likely be stuck with some 400 amp gear.