400 Amp MOCPD Feeding a 200 Amp MOCPD

Status
Not open for further replies.
All –

We are completing the retail power distribution for a mixed use, multi-family project in San Diego, CA.


Here's the scenario:

We have a 1200 amp switchboard with an 800 and a 400 amp retail meter and breaker. The 400 amp meter/breaker is supplying power to a 200 amp MOCPD downstream.

Is there any code violation with feeding the smaller breaker with the larger?

See below for a screenshot from the plans. I highlighted the setup in question.

Thanks for the help!

Screen Shot 2017-10-20 at 4.11.43 PM.jpg
 
No, there is no issue with a smaller breaker downstream of a larger breaker. Panelboards are required to be protected with upstream overcurrent protection having a rating not greater than that of the panelboard. This is provided by the 200A main.

There is however an issue with the 400AT breaker protecting a set of 400kCMIL conductors assuming the likely case that you are using 75C conductors and terminations for an ampacity of 335A. Look at 240.4(B) and 204.6.
 
Thank you for the reply.

As for the feeders, that "4WG400" on the 1-line is a feeder identifier on the feeder schedule for a 400 amp MOCP. On the feeder schedule on the plans, "4WG400" identifier calls for (2) 4# 250 KCMIL AL + Ground for the feeders. That should give us 410 amps of wire. Sound right?
 
Thank you for the reply.

As for the feeders, that "4WG400" on the 1-line is a feeder identifier on the feeder schedule for a 400 amp MOCP. On the feeder schedule on the plans, "4WG400" identifier calls for (2) 4# 250 KCMIL AL + Ground for the feeders. That should give us 410 amps of wire. Sound right?

Assuming they are ran in separate conduits where derating will not apply.
 