Plus I somehow missed that this is a feeder and not a service. You will have to parallel the run if it is a feeder. 225.30 only permits a building or structure to be supplied by one feeder or branch circuit. By joining the conductors together at both ends, they are considered one conductor, if they are not joined together at both ends they are not parallel conductors per definition and are considered multiple conductors - that is where the violation of 225.30 would be. You can still have up to six disconnecting means, and must group them together, but you have to supply it with a single feeder.
The OP said this was a service lateral. He did not say if the conductors were in conduit or if they were in the same conduit.