Up to six sets like this (plus exceptions for fire pumps, emergency, stanby...) is still considered only one service. One service can have up to six disconnecting means plus exceptions for fire pumps, emergency systems .... and a few other special items.
To be parallel the conductors must be joined together at both ends. Does not even need to be a panel bus or MB that they are joined by.
The complication with the OP is whether or not we can have additional service disconnecting means at separate structures supplied from the same service drop, lateral, or other point in the service, the run to the house is just fine if it were the only thing supplied.
Thankyou I knew there was a stipulation regarding parallel conductors. Thanx for the clarification. But looking through 230 it really doesn't say much about this type of application. I see the six disconnect rule and am familiar with that however from what I understand is that rule is there to provide a central point of disconnection in the event of an emergency for the building being served, not the out building that may have no relevance with the building being served (point of attatchment). The building that is being tapped too is concerning to,how would anyone know where to shut its power off externally if the service conductors terminate within the structure. Also will there be interconnection of water lines between the buildings, bringing up a neutral issue like paralleled neutral currents. I guess that signage would need placed regarding disconnection means and feeder origination and atleast a disconnect on the outside of the out building. I think POCO would be more informative on this question since its their unprotected conductors at risk. just my thoughts thanx.
P.S. I have run into some services that have 2 barrel lugs on load side of meter 1 feeding the structure its attatched to and the other in conduit to garage.
Last edited: