Jimmy7
Senior Member
- Location
- Boston, MA
- Occupation
- Electrician
I’m about to do this 400 amp service for a single family home. Can I run what I’m going to do by you.
1. I was going to run three 600 al XHHW underground outside.
2. I’m going to install a meter socket that has two 200 amp breakers with a barrier. The meter socket states 320 amps, is that okay? I’m going from 200 amps to 400 amps due to geothermal equipment, but it’s not too much additional load.
3. I was going to run 3/0 Ser copper ground from the Two 200 amp breakers in the meter socket to two 200 amp main breaker panels (Separating the grounds and the neutrals).
4. I was going to run a 1/0 copper ground from the water meter to the meter socket.
5. I was going to run a number 6 copper ground from the meter socket to two ground rods.
1. I was going to run three 600 al XHHW underground outside.
2. I’m going to install a meter socket that has two 200 amp breakers with a barrier. The meter socket states 320 amps, is that okay? I’m going from 200 amps to 400 amps due to geothermal equipment, but it’s not too much additional load.
3. I was going to run 3/0 Ser copper ground from the Two 200 amp breakers in the meter socket to two 200 amp main breaker panels (Separating the grounds and the neutrals).
4. I was going to run a 1/0 copper ground from the water meter to the meter socket.
5. I was going to run a number 6 copper ground from the meter socket to two ground rods.