jefftaman said:I have not seen the panel, I do know it is a Cutler/Hammer 400 amp service. The issue is our local POCO has 2/0 for the service drop and they said they cannot connect to the 400 kcmil. The homeowner's electrician is arguing that since there is not a 400 amp main but rather (2) 200amp mains tied together the service entrance conductors only need to be 2/0, since the SEC's will go to a 200 amp breaker not a single 400 amp main. I hope this makes sense.
jefftaman said:The issue is our local POCO has 2/0 for the service drop and they said they cannot connect to the 400 kcmil.
dezwitinc said:Stickboy,
Is this what you are talking about?
http://www.milbankmfg.com/Products/Catalogs/CatalogFiles/PDF/320 MBC 08-05R.pdf
chris kennedy said:They can and they will. Ask to speak to someone else.
What about the grounded conductor potentialjefftaman said:This is a residential 400 amp overhead service, this guy has a christmas light display beyond belief. I have not seen the panel but I will call the guy on Monday to go take a look. He is stating one 200 amp breaker feeds one bus and the other 200 amp breaker feeds the other bus, the breakers are tied together. So theoreticaly each ungrounded SEC will never be subjected to more than 200 amps, which is why he arguing that he only needs 2/0. If this had a 400 amp main then it is a no brainer, but the two 200 amp mains is throwing me for a loop.
normbac said:What about the grounded conductor potential
Still sounds like a 200amp service...Are they single pole 200's (have never seen one)? Since the each only feed one buss? Something just doesn't sound right here.....jefftaman said:This is a residential 400 amp overhead service, this guy has a christmas light display beyond belief. I have not seen the panel but I will call the guy on Monday to go take a look. He is stating one 200 amp breaker feeds one bus and the other 200 amp breaker feeds the other bus, the breakers are tied together. So theoreticaly each ungrounded SEC will never be subjected to more than 200 amps, which is why he arguing that he only needs 2/0. If this had a 400 amp main then it is a no brainer, but the two 200 amp mains is throwing me for a loop.
It's a single phase 320amp meter socket. 80% of 400 is 320 so it can be used to meter a 400amp single phase servicegoldstar said:I'm trying to follow this thread and I'm confused about a few things :
1) Is this a 400 amp overhead service in a residential area ? Haven't seen too many of those.
2) If so, most of the POCO's that I deal with carry insulated barrel crimps on their truck that are suitable for up to 2/0 copper. They can't crimp onto 4/0.
3) If you've calculated for a 400 amp service then shouldn't the feeders for the "total" service have to be sized for 400 amps ?
4) If you've calculated for a 400 amp service how can you use a disconnect that is rated at 320 amps ?
Any 400 amp (or greater) services that I've done have been fed underground into a CT cabinet with a special POCO wired meter socket. Once you leave the CT cabinet and wire into 200 amp main disconnects you can use 2/0.
If I'm looking at this in a wierd way or not thinking "out of the box" would someone please say so and point me in the right direction ?
jefftaman said:This is a residential 400 amp overhead service, this guy has a christmas light display beyond belief. I have not seen the panel but I will call the guy on Monday to go take a look. He is stating one 200 amp breaker feeds one bus and the other 200 amp breaker feeds the other bus, the breakers are tied together. So theoreticaly each ungrounded SEC will never be subjected to more than 200 amps, which is why he arguing that he only needs 2/0. If this had a 400 amp main then it is a no brainer, but the two 200 amp mains is throwing me for a loop.