400 amp service w/(2) 200 amp main breakers

Status
Not open for further replies.
jefftaman said:
This is a residential 400 amp overhead service, this guy has a christmas light display beyond belief. I have not seen the panel but I will call the guy on Monday to go take a look. He is stating one 200 amp breaker feeds one bus and the other 200 amp breaker feeds the other bus, the breakers are tied together. So theoreticaly each ungrounded SEC will never be subjected to more than 200 amps, which is why he arguing that he only needs 2/0. If this had a 400 amp main then it is a no brainer, but the two 200 amp mains is throwing me for a loop.

If this is the same panel I have seen, Each 200 amp breaker is a 2-pole (240v) Feeding onto two seperate sets of bussing. both Have the A & B leg in them. If fully loaded the panel has the capasity to draw 400 amps through the service entrance conductors.
 