- Location
- Chapel Hill, NC
- Occupation
- Retired Electrical Contractor
suemarkp said:I can't seem to follow what you're writing.
The op stated this
I was surprised and angry to find a 400amp 40circuit panel with no main breaker.
suemarkp said:I can't seem to follow what you're writing.
I was surprised and angry to find a 400amp 40circuit panel with no main breaker.
M. D. said:He then said it was filled to capacity, which I take to mean that it is incompliance but should one add another breaker it will be in violation
romeo said:Thank you for your response. That is what I am doing now, I expect to hear from the power company Eng. tomorrow.The breakers have 10,000 AIC rating,if the available fault current does not exceed 10,000 the service will pass.
Just to let everyone know, I am not a this is my town kind of inspector, if I am not able to provide a code section that has been violated I will pass the job.
Now I am going to give everyone a Chance to blast me again. Does anyone agree that someone down the road will install a seventh breaker in that 42 circuit panel? I know I need to inspect by code and stop all this thinking, and that is just what I do.
dnem said:How this "combination of switching units that can be mounted" would apply to a 12 slot panel is unclear, but the 42 slot MLO panel is obviously not being used according to the manufacturers UL listing instructions when used as a main.
According to the information you've given so far, this is not a code compliant installation. . The violation is 110.3(B), "Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling."
tadavidson said:What If?
"Down the road' A jack leg handyman or such comes in and in the course of a repair removes the egc. from a metal framed machine or puts two white wires under the same screw or removes a 20 amp breaker and puts the 12 awg under the lugs of a 50 amp breaker cause that all he had on the truck or trunk of his/her car or what if a midget came riding in on an elephant and ....
Please!
tadavidson said:That is why inspectors or fire marshalls need to do or be allowed to do follow up inspections of all systems and If violations are found gig the owner and shut power down if not corrected in timely manner. I live in an area where in restaurants supply exit signs on drop cords mounted to the wall with tape. Where you can stand on someones new deck and touch the service tap. can I come down now?
liscense (inside joke)
petersonra said:What if a "real" electrician does the same thing? Does that make it somehow better?
Ever hear of the bill or rights? This is America. we don't allow government agents to search us or our property just because we might be doing something wrong.
LawnGuyLandSparky said:I agree, and they can violate my 43rd circuit when they pry the "non-ctl use" piggyback breaker out of my cold, dead, 40-ckt 200a Murray panel!
petersonra said:Ever hear of the bill or rights? This is America. we don't allow government agents to search us or our property just because we might be doing something wrong.
An 18-space panel is the largest that could meet this description, with six 3-pole breakers. A 12-space would be maxed with six 2-pole breakers.dnem said:See the UL Whitebook Panelboard Marking Guide in the back of the Whitebook. . If you're looking at the 2006 edition, page 9 of the Panelboard Marking section, item20A reads, "There must be at least one combination of switching units that can be mounted to occupy all available space for switching units; and, whether by using handle ties or similar devices, not more than six main disconnects will result (including factory installed disconnects)."
How this "combination of switching units that can be mounted" would apply to a 12 slot panel is unclear, but the 42 slot MLO panel is obviously not being used according to the manufacturers UL listing instructions when used as a main.
If the "suitable for use as service equipment when . . . " is on the label, it's compliant. From what you're saying, an 18-space ML panel is the largest UL should allow to have such a label.According to the information you've given so far, this is not a code compliant installation. . The violation is 110.3(B), "Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling."
LarryFine post #31 said:dnem said:See the UL Whitebook Panelboard Marking Guide in the back of the Whitebook. . If you're looking at the 2006 edition, page 9 of the Panelboard Marking section, item20A reads, "There must be at least one combination of switching units that can be mounted to occupy all available space for switching units; and, whether by using handle ties or similar devices, not more than six main disconnects will result (including factory installed disconnects)."
How this "combination of switching units that can be mounted" would apply to a 12 slot panel is unclear, but the 42 slot MLO panel is obviously not being used according to the manufacturers UL listing instructions when used as a main.
An 18-space panel is the largest that could meet this description, with six 3-pole breakers. A 12-space would be maxed with six 2-pole breakers.
dnem said:According to the information you've given so far, this is not a code compliant installation. . The violation is 110.3(B), "Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling."
If the "suitable for use as service equipment when . . . " is on the label, it's compliant. From what you're saying, an 18-space ML panel is the largest UL should allow to have such a label.
M. D. said:So David in your opinion ,...this 400 amp 40 circuit panel cannot be marked;
?Suitable for use as service equipment when not more than six
main disconnecting means are provided????
I can't think of any combination of 6 handels that would fill such panel.
tadavidson said:What If?
That is why inspectors or fire marshalls need to do or be allowed to do follow up inspections of all systems and If violations are found gig the owner and shut power down if not corrected in timely manner. I live in an area where in restaurants supply exit signs on drop cords mounted to the wall with tape. Where you can stand on someones new deck and touch the service tap. can I come down now?
liscense (inside joke)petersonra said:What if a "real" electrician does the same thing? Does that make it somehow better?
Ever hear of the bill or rights? This is America. we don't allow government agents to search us or our property just because we might be doing something wrong.
dnem said:If the manufacturer put that sticker on a 40 slot MLO, it would be a violation of the listing.
Manufacturers can make mistakes just like the rest of us. . 110.3(B) applies to everybody including the factory workers making the panels.
Please do not confuse the issue with facts!iwire said:David, Larry. I would say that 18 is not the limit.
Some shunt trip breakers use 4 spaces, that brings us to 24 spaces needed to reach six disconnects.
LarryFine said:Please do not confuse the issue with facts!![]()