I am installing a 400 amp service in a commercial location. Utility is providing the underground lateral. I have two 200 amp panels internally. I researched 310-16 and it looks as I should come out of the meter to each disconnecting means with 3/0 feeders. Each internal panel has a 200 amp main also. I was going to nipple from the meter base with 2" to disconnects outside. The panels are about 30 feet internally. I believe I need the external 200 amp disconnects. Should I use 200 amp main lug panels or stay with the main breakers there also.
Sent from my iPhone using Tapatalk
Just wondering, wouldn't the meter go outside and the 2 trailer panel service discos immediately inside? Then just 4 wire feeder to the subpanels, no main disco required (but you can if you want).
I do think you need 4/0 Al for the 200A entrance cable. Maybe the 3/0 is ok for feeders to the subpanels?
I get that he is installing the discos outside, and there will be 2 disconnects, but wouldn't those be called Service disconnects rather than Main disconnects?The op is install outdoor trailer panels with a main in each and feed thru lugs. He is not using a main disconnect but rather 2- 200 amp breakers as his disconnecting means.
3/0 al is not okay to the subpanel if you are using feed thru lugs. Even the 4/0 is only good for 180 amps but we are allowed to use the next size up breaker (200 amps) as long as the calculated load is 180 amps or less
Dennis said 3/0 aluminum would not be acceptable. Pretty sure when OP mentioned 3/0 he was using copper, but did not specifically mention copper or aluminum either.I get that he is installing the discos outside, and there will be 2 disconnects, but wouldn't those be called Service disconnects rather than Main disconnects?
Also, and with respect, I don't understand your previous post re 3/0 "The main disconnects must be main breaker or a max of 6 disconnects. I usually use a wp trailer panel. This has 8 cir. plus feed thru lugs that you use to feed the indoor panels. 3/0 is sufficient
Pretty sure when OP mentioned 3/0 he was using copper,
Dennis said 3/0 aluminum would not be acceptable. Pretty sure when OP mentioned 3/0 he was using copper, but did not specifically mention copper or aluminum either.
You must mean post #4. Page number doesn't mean so much since you can change how many post are on one page, I currently have all the posts so far on a single page, you can set it up to 40 posts per page.Looks to me like Dennis's post page 1 specifically says 3/0 is sufficient. No biggie.