He mentioned the side windows preventing fitting both panels back-to-back to the meter, so back-to-back is obviously an option. My suggestion means that only the meter would have to be outside.
That's one of those tricky placement issues that would require work to convince a spotter. They don't like any meter facing the front or rear property lines. Only on the side
 
I'm curious. The house doesn't look too large, why the 400 amp? What kind of load? Prepping for EV charging? Or is there more than visible in the picture. Just wondering with all the efficient things being produced now. Thanks
 
I'm curious. The house doesn't look too large, why the 400 amp? What kind of load? Prepping for EV charging? Or is there more than visible in the picture. Just wondering with all the efficient things being produced now. Thanks
It's about 4500 sf on 1st and 2nd floors. It's 5 bed 6 bath right now with future basement finish.

I did a quick run through what I know and came up with 230 amps

Dual fuel range, wall oven/micro combo, 2 AC,
2 laundry

And I figured a car charger because there are a lot of them in this neighborhood and surrounding.
 